    What would be the best way to wire-up heat tape in a propane filling area?

    What would be the best way to wire-up heat tape in a propane filling area?

    I have a customer that needs a heat tape added to a Vacuum pump. (cold weather/oil is creating high amps overload).

    Would a simple EXP switch, and, then connect the heat tape (through a CGB) into a round EXP screw cap box be sufficient? Where would Seal-offs be needed?

    Thank you for your time

    Dennis

  2. #2
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,731
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Seal offs would be needed where it exits/enters the hazardous zone.
    "Just because you're paranoid, doesn't mean they're not out to get you"

  3. #3
    Join Date
    Aug 2011
    Location
    NH
    Posts
    252
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Chromalox and Thermon make heat trace listed for Class I Div 1 and Div 2 locations.