    Placing Neutrals Under Added Ground Bar in Main Panel

    100a main panel, there were not enough spots on ground bars that came premounted on panel. They had to add an additional ground bar to the panel to fit the rest. The only way the ground bar is connected electrically to the main neutral is through the panel enclosure, and it is secured to the enclosure with two machine screws. Is it okay to have neutral wires under this ground bar considering that there is going to be current passing through the panel enclosure to the neutral lug at any given time? Is this a hazard?

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,401
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Steve98 View Post
    Is it okay to have neutral wires under this ground bar considering that there is going to be current passing through the panel enclosure to the neutral lug at any given time? Is this a hazard?
    No and yes. The EGC's may use the enclosure as part of their pathway, but not the CCC's.

    Best to move existing EGC's from real neutral bar to new bar, and use those holes for new neutrals.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA