    Article 409.20 conductor-minimum size and ampacity

    Article states...the size of the industrial control panel supply conductor shall have an ampacity not less than 125% of full load current rating of all heating loads plus 125% of the full load current ratings of all other connected motors and apparatus based on their duty cycle that may be in operation at the same time.

    So if I have 4 heaters that come on at same time 7amps for each one.

    7x4=28
    Is it 28x1.25=35 for heating loads

    Sent from my Moto Z (2) using Tapatalk

  2. #2
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    1,151
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yep