    "Individual Branch Circuit" for fridge.

    This is a spinoff of this thread:
    https://forums.mikeholt.com/showthread.php?t=195421

    Taking into consideration Exception 2 to 210.52(B)(1) and the definition of "Branch Circuit, Individual," is it allowable to use a 15 amp circuit to serve a duplex outlet located behind, and intended to power, the fridge?

    Many of us have commented on this topic before. Many have said that if you use a simplex you are compliant, but if you use a duplex you will be outside the definition. The reasoning I have read is that a duplex receptacle comprises two "outlets." I am no longer certain that a duplex could not be used in this situation. My reasoning is that the definition says that the circuit serves "only one utilization equipment." It does not say "only one outlet." The other half of a duplex located behind the fridge is essentially useless. I submit that that receptacle is only serving "one utilization equipment," namely the fridge.

    By the way, I will be opening a new thread in Campfire Chat to describe our wiring woes.

    I am submitting this now because we are undergoing a total kitchen remodel. It has evolved into a 100% rewiring project for the kitchen. I have not asked the electrician what he plans to use to feed the fridge. He has already installed the outlet box in the wall, and I am willing to bet he is not planning to install a simplex. But I don't know whether he is planning to use a 15 or 20 amp breaker.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,945
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Individual 15A branch circuit and a duplex recpt is ok IMO.
    If you don't think too good, don't think too much.

  3. #3
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,445
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    FWIW, '17 has different wording for the exception:
    Exception No. 2: In addition to the required receptacles specified by 210.52, a receptacle outlet to serve a specific appliance shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.

    It does, however, still use the word "receptacle outlet (singular) which would seem to support a simplex outlet IMO.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  4. #4
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,438
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Gus, I will counter that by saying that nobody, and I mean absolutely nobody, ever uses the plural "receptacles," when talking about a duplex.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  5. #5
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,438
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    FWIW, '17 has different wording for the exception:
    Right. The 2014 allowed this for just the fridge.

    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  6. #6
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,445
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by charlie b View Post
    Gus, I will counter that by saying that nobody, and I mean absolutely nobody, ever uses the plural "receptacles," when talking about a duplex.
    I agree and I imagine a huge percentage of the installs have a duplex...and I have never rejected the instal,l but I think the actaul wording calls for a simplex.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  7. #7
    Join Date
    Apr 2017
    Location
    Boston, MA, USA
    Posts
    85
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I just want to mention that Massachusetts has an amendment which covers this:

    "210.21(B). Insert a new fifth paragraph as follows:
    (5) Receptacles on Individual Branch Circuits. A receptacle outlet installed to comply with a requirement for an individual branch circuit shall contain a single receptacle, or a multiple receptacle if, and then only to the extent that, the supplied equipment includes multiple supply cord connections. "

  8. #8
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,445
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Leespark57 View Post
    I just want to mention that Massachusetts has an amendment which covers this:

    "210.21(B). Insert a new fifth paragraph as follows:
    (5) Receptacles on Individual Branch Circuits. A receptacle outlet installed to comply with a requirement for an individual branch circuit shall contain a single receptacle, or a multiple receptacle if, and then only to the extent that, the supplied equipment includes multiple supply cord connections. "
    Have to read that a couple of times for it to sink in but makes sense (maybe because it supports my thoughts )
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  9. #9
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    8,098
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Do you have a spec book you will give to the contractor?
    Moderator-Washington State
    Ancora Imparo

  10. #10
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,759
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by charlie b View Post
    The reasoning I have read is that a duplex receptacle comprises two "outlets."
    To me, a duplex receptacle is two receptacles in a single outlet.

    I don't know whether he is planning to use a 15 or 20 amp breaker.
    You can always ask, can't you?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •