    I have 277V to 120V, 2kVA, single phase transformer. I have provided the grounding electrode conductor to grounding electrodes however, I am wondering if it requires neutral to ground i.e. system bonding jumper NEC 2014 250.30?
  2. #2
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,184
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Based on 250.21(B) I would say "yes" but more detail might be warranted.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  3. #3
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    185
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    250.21(b) is ground detectors???
    Sent from my SM-G935U using Tapatalk
  4. #4
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,184
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    opps 250.20(B) (either ignorance or a typo )
  5. #5
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    185
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Its step down transformer 277V To 120V Hammond power C1F1C003WES 3KVA 1PH Transformer.
  6. #6
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,184
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I can not think of a reason for there not to be a bonding jumper looking at 450.6 & 250.20
  7. #7
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,805
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, you will need to make this a grounded system. If it is straight 120 volt ground one end of the secondary winding. You will have the full 3 KVA output at 120 volt. If this is a 120/240 unit you could ground the mid point but you will only get 1/2 the output on each leg.
    One advantage if it is straight 120 volt or (you connect it that way) is you could possibly omit secondary protection.