Underground access?

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Can a cover for a conduit bend be partially underground? Does this create any issues with respect to required access?
 

Attachments

  • DSCF2809.jpg
    DSCF2809.jpg
    148.8 KB · Views: 0

resistance

Senior Member
Location
WA
Violation of 314.29—as I believe that specific conduit body is not listed to be installed underground in that position.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It is also not accessible without tools for digging or strong fingernails, but the code may not take issue with that since the building finish is not involved. :)
 