    This is along the lines of this topic https://forums.mikeholt.com/showthread.php?t=195503 but I didn't want to hijack it.
    This is actually a topic on another board. There are two attached town houses and both are fed from a single service line and regulator with a manifold supplying two gas meters. One meter for unit #1 and the other for unit #2. The outlet side of the meters go off to their respective units.
    The problem arose when the owner of unit #1 was having a gas fireplace installed and the plumber, in disconnecting the gas line within the unit noticed a spark. This prompted him to tell the homeowner and call the gas company. Apparently there is an intermittent voltage of between 12-24V on unit #2s gas line after the meter was removed. I haven't been able to get an answer as to where that voltage was measured to from the gas line or what kind of meter was used. It very well may be that unit #1 us causing the problem. But the gas company did leave the meter for unit #2 disconnected and posted a turn off notice on the door indicating that the homeowner of unit #2 is to have an EC remedy the problem before they will re-install the meter. (It seems those people are out of town on vacation.)
    My reply was that I don't think 12-24V would be unusual given that the gas lines in each unit is bonded to their respective neutrals and you are seeing much the same as the circulating currents on a common water service. I did say that I would check for a compromised service neutral but that's about it.
    What do you think?
    -Hal
  2. #2
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,741
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Sounds like the pilot was attempting a relight, or the burner itself with hot surface ignition
    Tom
    TBLO
  3. #3
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,746
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I wonder if a gas furnace control transformer could be the source of the voltage? Turning off the furnace circuits could be tried while observing the voltage.
    Also, compare each side of the open gas connection to the electrical and/or water grounds to wee what is actually energized.
    It could be that the incoming gas is at zero volts, and a houses GES is what is energized, possibly due to a poor electrical neutral.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  4. #4
    Join Date
    Jun 2003
    Posts
    4,352
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    That's what the OP of the original thread said, I can't see how that could happen especially if the gas line is bonded to the GES. And how would that be a hazard anyway? I don't know where that theory came from. Probably because it's 12-24V. He also thinks his house would have blown up.
    I'm sticking to my story about a possible poor service neutral for one of the units, particularly because it's intermittent, it varies in voltage and there is enough current to generate a spark. Other than that I believe it's normal.
    -Hal
  5. #5
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,746
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hbiss View Post
    Abby Normal?
    Larry B. Fine
    Master Electrician
    Richmond, VA
  6. #6
    Join Date
    Jun 2003
    Posts
    4,352
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Abby Normal?
    Dunno, is it? Take a look at this thread and tell me how metallic gas distribution would be different: https://forums.mikeholt.com/showthread.php?t=194935
    Quote Originally Posted by winnie View Post
    Generally not a concern if you are an electrician and are not seeing any problems.
    But it is a concern if you are a plumber. As mentioned above, common water piping between buildings can form a low resistance parallel path for neutral current. In some cases plumbers have experienced electric shock when cutting water pipes used as ground electrodes.
    Quote Originally Posted by kwired
    Current follows all possible paths, the majority of the current takes the lowest resistance path. A network of metallic municipal water piping may very well be just as low of resistance or even lower in some instances than the service neutral and I could see it easily carrying around same amount of current as the service neutral in that situation.
    I believe we don't frequently see stray voltage problems on gas lines because gas companies use plastic and dielectric couplings.
    -Hal
  7. #7
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,746
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    A gas piping system could become energized from one of the gas appliances. That's what made me think of a furnace transformer when 24v was mentioned.
    I'm thinking of this as a bonding issue.
    Larry B. Fine
    Master Electrician
    Richmond, VA
  8. #8
    Join Date
    Jun 2003
    Posts
    4,352
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Usually 24V control circuits float- one side is not grounded. However I would have to look at the wiring diagram of the specific piece of equipment to say that with certainty. But then there is the varying 12-24 volt issue that wouldn't fit that theory.
    Also remember that this is all second hand information coming from a customer. I have a feeling that gas companies are overly cautious when they get customer complaints about perceived safety issues these days because of the incident in Mass.
    -Hal
  9. #9
    Join Date
    Jun 2003
    Posts
    10,741
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    -Hal
    I’ve never put a meter on an disconnected gas line to see what the voltage was while the furnace was attempting ignition. Never entered my mind that I should. I’ve never put a meter on one conductor of an open paralleled connection. I suspect that voltage would be close to zero, but would still spark when connected. That leads me to believe that the gas line interior to the units is serving as a ground loop. I didn’t look back to see who already mentioned that. Open one end, you get the spark. The 12-24v would be from one of the furnace ignition. Maybe both.
    Customer supplied information, as you know, needs to be taken with a grain of salt. “My husband was hanging these shelves when the circuit breaker started tripping.” was used with no further explanation required. Seldom the case.
    Tom
    TBLO
  10. #10
    Join Date
    Jun 2003
    Posts
    4,352
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Neither have I, you never hear much about gas except for CSST in this trade. This is also the same as all those situations where there is sparking when connecting a cable box or the drop cable burned up. Many, including myself advocate an isolator before the cable ground block.
    For gas lines there is this https://www.dresserngs.com/sites/def...GS-DPS-016.pdf
    -Hal