    SEC routing

    I have no pics for this:

    1. Attached garage right side of home.
    2. Meter and main disconnect on outer right wall.
    3. Main panel is in the basement, which would be on the left side of the garage, 1 floor down.
    4. Garage converted to living space by framing a floor and creating a 18" or so crawlspace over the original floor slab.
    5. No access to the crawlspace.
    6. SEC from the outside main travels through this crawlspace (about 20 feet) to the basement panel.

    My question, is it OK for SEC to be inaccessible like this?
    Tony Shupenko, PE

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,358
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Cables do not need to be accessible just the equipment and splices if there are any
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,333
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    They are not SEC if there's a disconnect, it's a feeder
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #4
    Join Date
    Nov 2003
    Location
    New Jersey
    Posts
    657
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks
    Tony Shupenko, PE

  5. #5
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,358
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    They are not SEC if there's a disconnect, it's a feeder
    IMO, SEC is service entrance cable-- it can be SEU or SER.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  6. #6
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,333
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    IMO, SEC is service entrance cable-- it can be SEU or SER.
    Fair enough. I was thinking "service entrance conductors". Just wanted to make sure the right terms were being used
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  7. #7
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,358
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Fair enough. I was thinking "service entrance conductors". Just wanted to make sure the right terms were being used

    I assumed that was what Tony meant. I hope se conductors are not run exposed in the crawl space.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky