Thread: New service rated main breaker transfer switch- sub panel grounding question

  1. #1
    chas1776 is offline Inactive, Email Never Verified
    Join Date
    Feb 2004
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    New service rated main breaker transfer switch- sub panel grounding question

    We are installing a generator with a 200 amp service rated main breaker transfer switch at the electrical meter location. The existing configuration, the feeders from the meter go directly underground in a 2" PVC conduit 70' across the home an up to the 40 circuit panel with a 200 amp main breaker. Now that we have moved the main breaker outside next to the meter can we have to separate the grounds and neutrals in the existing panel.

    My question is, do we have to pull out the 2/0 feeders and add the #6 THHN copper ground through the same conduit as the feeders or can we run the the #6 THHN copper ground through the attic and bring it to the panel that way separately from the feeders? Not sure how difficult it will be to remove the feeders since they been in the conduit for 20 years.

    Thanks,

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,608
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The EGC for the feeder must be in the raceway with the feeder conductors. At least you have a raceway to work with and not a 3 wire cable which would need to be replaced with a 4 wire. Pulling out the conductors and adding the EGC shouldn't be too difficult with a relatively short run.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,256
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I would attempt adding the EGC without pulling the existing conductors first.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  4. #4
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,185
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    All you need is "because infinity said so" :-) but if you want a Code reference it's 300.3(B)