    Radius of 4in of EMT 90 for 10 K volts thee 500 mcm

    What size 90 degree radius is required for 10,000 volts for thee 500 in 4 in emt

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,185
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Depends on the type cable.. see 300.34
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,608
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    Depends on the type cable.. see 300.34
    Wouldn't a standard 4" elbow comply with that section?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,905
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Wouldn't a standard 4" elbow comply with that section?
    A standard radius bend for 4" is only 16". The first 500kcmil, shielded cable I found in a quick search has an OD of 1.570. 300.34 gives the minimum bend radius for shielded conductors as 12 times the diameter, requiring a minimum radius of 18.84".
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,608
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    A standard radius bend for 4" is only 16". The first 500kcmil, shielded cable I found in a quick search has an OD of 1.570. 300.34 gives the minimum bend radius for shielded conductors as 12 times the diameter, requiring a minimum radius of 18.84".

    Good to know.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,568
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Now go look up how to size the pull boxes.

  7. #7
    Join Date
    Jun 2003
    Posts
    6,952
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sameguy View Post
    Now go look up how to size the pull boxes.
    I'd also double check the 4" conduit size, and the jambing ratio.

  8. #8
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,185
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    4" EMT Long Radius elbows have a 24" radius
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  9. #9
    Join Date
    Jun 2005
    Location
    Massachusetts
    Posts
    1,596
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by steve66 View Post
    I'd also double check the 4" conduit size, and the jambing ratio.
    Consider 5” conduit. The wires can’t jam in 5”. Jamming can be a nightmare.

  10. #10
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,568
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    5" could take new tooling if he doesn't have them.