    Grounded Conductor from Power Company Transformer

    We have an industrial customer who is having the Power Company replace a 480 volt 3 Phase 3 Wire Delta transformer with a 277/480 Volt 3 Phase 4 Wire Wye Transformer. The customer has their own Electricians, but want our Company to help them with upgrading the Service Conductors and termination. This is a Customer Owned Service from the Power Company's Transformer into the facility. Their electricians are indicating they do not need the grounded conductor ran with the phase conductors, as they do not want to increase the size of the existing conduits. We are hesitant on this installation, because we feel the grounded conductor needs to be installed in order to clear a fault. Are we correct in our interpretation? Thank you for your help!

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,608
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The grounded conductor is required for a 480Y/277 volt service. It can be smaller when sized according to 230.42(C).

    Welcome to the Forum.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,479
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    And there is also 250.24(C)

    Roger
    Moderator

  4. #4
    Join Date
    Apr 2006
    Location
    Springfield, MA, USA
    Posts
    3,426
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A perhaps useful question is 'where can the grounded conductor stop and egc only be run with the phase conductors'?

    If a load doesn't require a neutral, you don't have to run it. If the facility was previously supplied with a delta, then nothing uses the grounded conductor as a supply conductor. The only reason for the grounded conductor in this case is fault clearance.

    -Jon

  5. #5
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,809
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ranger519 View Post
    We have an industrial customer who is having the Power Company replace a 480 volt 3 Phase 3 Wire Delta transformer with a 277/480 Volt 3 Phase 4 Wire Wye Transformer. The customer has their own Electricians, but want our Company to help them with upgrading the Service Conductors and termination. This is a Customer Owned Service from the Power Company's Transformer into the facility. Their electricians are indicating they do not need the grounded conductor ran with the phase conductors, as they do not want to increase the size of the existing conduits. We are hesitant on this installation, because we feel the grounded conductor needs to be installed in order to clear a fault. Are we correct in our interpretation? Thank you for your help!
    Was the old xformer corner grounded or ungrounded? Is the POCO grounding the new xformer X0 point (very likely)?
    If the POCO is supplying a grounded Y then you must bring the neutral to the service disconnect. If you old system was corner grounded this is going to be a big problem.

  6. #6
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,185
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    POCO is the key ! Locally we have had a few of those situations and POCO did not ground XO at there transformer thus it remained an ungrounded system.
    Not sure if that has effect on their transformer and obviously itys up to your POCO but if they ground XO you must bring it to the service by Code as mentioned above.