Thread: Con-Edison end box

  1. #11
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,225
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by defishu View Post
    Attachment 22074the left conduit is feeding a 600 amp service switch, the top 2 are feeding a 800 amp service switch, and there is a small one on the right feeding a 200 amp switch. I feel like this is a sub end-box. The main end box is above this one.
    I see an additional 600-800 amp service with a separate meter in the left of the photo. The 10 point meter pan for the CT cabinet is to the right of the CT cabinet.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #12
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,535
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by defishu View Post
    Uggggh! Don't think I would go in there without a hazmat suit. Get flooded much? Do a load calc and redo that disgusting mess. Then you won't have to worry about the size of what's there.

    -Hal

  3. #13
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,225
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    You really need a photo with the cover off of the end box to confirm what's actually there. It appears that there are actually 3 services, the ~600-800 one to the left with it's own meter, the 400 amp(?) CT service and the ~200 amp to the right with it's own meter. Each one is spliced and fed from the end box therefore the CT cabinet is not feeding all of the service disconnects.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #14
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,909
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    You really need a photo with the cover off of the end box to confirm what's actually there. It appears that there are actually 3 services, the ~600-800 one to the left with it's own meter, the 400 amp(?) CT service and the ~200 amp to the right with it's own meter. Each one is spliced and fed from the end box therefore the CT cabinet is not feeding all of the service disconnects.
    Looks that way to me as well. 1 CT meter and 2 direct meters. Kind of a scary looking room.

  5. #15
    Join Date
    Oct 2015
    Location
    US
    Posts
    944
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Knowing how Con Ed operates they could be anything from #2-3/0

    Sent from my SM-G965U using Tapatalk

  6. #16
    Join Date
    Feb 2018
    Location
    new york
    Posts
    28
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by defishu View Post
    Attachment 22070
    can anyone tell me the what is the size of the incoming power from above picture. The only thing I know is the end box is feeding 3 service switches(One is 800 amp, one is 600 amp and the other one is 200 amp)

    there is no grounding wire??

  7. #17
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,225
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by defishu View Post
    there is no grounding wire??
    This service is a mess but there isn't supposed to be an EGC on the line side of the service disconnects. The metal component should be bonded to the neutral.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #18
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    1,306
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Rob, if I understood that right, that means that this is part of service and is not after the meters... which is where we ground, first disconnect after the meter... or is it Fuse or Breaker after the meter...lol
    Student of electrical codes. Please Take others advice first.