    When the load wiring is new (service change, new circuit, etc.), I routinely use my solenoid tester between a line-side hot and each load terminal to make sure that no load conductor is grounded before energizing.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  2. #12
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,392
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The only time I've been exposed to a serious arc flash event was when someone closed a breaker for the first time. I was working on a panel with a 600HP soft starter in it and I finished, so I told the guy in the other room that I was done and I started to close the doors of the panel. Just as the local disconnect handle interlock engaged with the door, he closed the breaker in the switchgear feeding the soft starter. The local disconnect was open, but they had nicked a LINE SIDE conductor in the conduit and it vaporized, blowing a fireball out at me. Because the doors were almost closed and the interlock held, the blast was deflected mostly up and down so it torched my boots and singed my eyebrows and hair where the safety glasses didn't cover. I did NOT, by some miracle, wet myself... Ever since then I always stand to one side rather than directly in front of anything.

    In the investigation as to how that nicked conductor was allowed to be there, turned out they meggered everything, then pulled the conductors BACK into the conduit in order to remove and re-install the back panel for the soft starter. But they failed to re-megger the conductors again, ASSuming they were OK after being pulled back into the conduits.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  3. #13
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,812
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Strathead View Post
    If all covers are in place, there should be no requirement for PPE and no more risk than that of getting struck by lightning on a sunny day. The only caveat would be a true bolted fault on a breaker who's AIC rating was calculated so incorrectly that the hedge factors in everything are overcome.
    That is a false statement unless the enclosure is arc rated

  4. #14
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    39,705
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I suppose there may be some increased chances of a fault from miswiring or bad equipment that "first time", though there is still risk anytime you turn it on. Even after there has been some kind of repairs done that risk may be a little higher the first time afterward. Testing for faults before turning on "the first time" should lower the chances, if you find and fix any faults indicated in the testing.

    Even on low incident energy applications (maybe typical dwelling or small commercial project) how often do you find something is faulted the first time you energize a circuit? Maybe not all that many times for most of us, but sometimes the fault isn't something we did but rather a defect in something and we never noticed until energizing it.
    I live for today, I'm just a day behind.

  5. #15
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    3,005
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by zog View Post
    That is a false statement unless the enclosure is arc rated
    Can you quote a source that requires PPE when all covers are in place?


    I know what I don't know, and I know where to go to find it!

  6. #16
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,039
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Seems the tenured sparks aways have their anecdotals.

    Myself i was blind for what was the worst 5 minutes of my life......so far...

    None of this is necessarily our own neglect , miswiring, whatever....

    You guys all know the 'ol bold electrician addage .....

    ~RJ~

  7. #17
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,912
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Strathead View Post
    Can you quote a source that requires PPE when all covers are in place?
    yeah. me.

    i closed a main breaker on a residential panel, with all the
    covers properly in place. the arc came crawling out between
    the cutout hole, and the edge of the breakers, burnt the skin
    off the back of the middle two fingers on my right hand..

    you need to wear PPE. you can quote me if you need to.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  8. #18
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    39,705
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Fulthrotl View Post
    yeah. me.

    i closed a main breaker on a residential panel, with all the
    covers properly in place. the arc came crawling out between
    the cutout hole, and the edge of the breakers, burnt the skin
    off the back of the middle two fingers on my right hand..

    you need to wear PPE. you can quote me if you need to.
    Yet we are required by code make these things readily accessible, which is also readily accessible to the unqualified, makes a lot of sense right?

    But OSHA is only for the employed, so what if others are in any danger I guess. Now comes the manager at an office building or other employee in similar situation that doesn't ordinarily do any electrical work tasks that tries to reset a tripped breaker in their office building - I guess we should at least be putting big warning signs on this equipment that only qualified individuals can even open the dead front cover and operate any devices inside, though I anticipate even that will get ignored most the time.

    Typical dwelling, the available incident energy isn't that high all that often to be able to do that, but sometimes it is.
    I live for today, I'm just a day behind.

  9. #19
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,392
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Strathead View Post
    If all covers are in place, there should be no requirement for PPE and no more risk than that of getting struck by lightning on a sunny day. The only caveat would be a true bolted fault on a breaker who's AIC rating was calculated so incorrectly that the hedge factors in everything are overcome.
    Quote Originally Posted by Strathead View Post
    Can you quote a source that requires PPE when all covers are in place?
    In Table 130.7(C)15(A)(a) where they provide the list of appropriate PPE for tasks, it says the following under the task of operating a circuit breaker:
    Under the column heading "Equipment Condition", no additional PPE is required only if;
    All of the following:

    The equipment is properly installed
    The equipment is properly maintained
    All equipment doors are closed and secured
    All equipment covers are in place and secured
    There is no evidence of impending failure
    But, under the following conditions, yes, PPE IS REQUIRED if:
    One or more of the following:

    The equipment is not properly installed
    The equipment is not properly maintained
    Equipment doors are open or not secured
    Equipment covers are off or not secured
    There is evidence of impending failure

    Should there be an injury and a door WAS closed, an OSHA inspector is going to demand DETAILED RECORDS of whether the equipment was properly installed and maintained. The reality is, almost NOBODY has records like that.


    And BEFORE that, they provide this "Informational Note"
    Informational Note No. 2: The collective experience of
    the NFPA 70E Technical Committee is that, in most cases,
    closed doors do not provide enough protection to eliminate
    the need for PPE in situations in which the state of the
    equipment is known to readily change (e.g., doors open or
    closed, rack in or rack out).
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  10. #20
    Join Date
    May 2011
    Posts
    4,964
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    One guy I worked with told a friend of his died after he left a wrench against the busbars in a residential panel and turned on the breaker. This was in the context of replacing a 200A main breaker on a resi panel and the guy stood to the side and used a broom stick to turn on the replacement. Just in case.

    It's not the breaker that will blow up, most times.