In some commercial applications, particularly the ones that involve the inverters outputting 277/480, not only do you get to do that, you might have to do that to achieve your desired DC capacity. The deal is, you're limited to 30 in series for the shutdown voltage to not exceed 690.12's limit, due to the default 1V/optimizer output.
It used to be the case that most dual module optimizers involved series connecting the modules. Now with the onset of the 2019 rule, limiting you to 80V within the array, the newest version of dual module optimizers are built for parallel inputs instead of series inputs.
Given that voltage is most sensitive to temperature rather than irradiance, it is less of a loss to connect dissimilarly oriented modules in parallel, than it otherwise would be for modules in series. Current is more sensitive to irradiance, which means all modules may operate as if they received the lowest irradiance among the ones in series. More advisible to parallel different orientations, than to series different orientations.
Once you have separate power processing zones (which optimizers are), the respective modules/groups of modules operate independently anyway.