    Looks like it's okay in 250.118 to use emt as a ground. Is it also code to run subpanel feeder circuit without a equipment grounding conductor as long as the wires are within emt pipe the whole way?
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    17,609
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yes; why would think it wouldn't be?
    Roger
    Join Date
    Dec 2011
    Wisconsin
    Posts
    623
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    To add to Roger's response, many studies have shown that a metallic raceway performs better at clearing a fault than a wire type equipment grounding conductor.
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,140
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    We use EMT as an EGC all of the time unless someone is paying for a wire type EGC in the raceway.
    Rob
  5. #5
    Join Date
    Mar 2003
    New England
    Posts
    13,801
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I don't get the obsession with wire EGC's. I always encounter EMT installations done from the 1960's to the 1980's and it never had a separate ground wire. Now it does.
  6. #6
    Join Date
    Apr 2009
    Posts
    117
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    emt as ground
    just seems weird, but ok. thanks
  7. #7
    Join Date
    Apr 2009
    Posts
    117
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    emt as ground
    I have probably spent too many years as a romex jockey.
  8. #8
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,938
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by difowler1 View Post
    Not weird at all. The size of EMT large enough for a given set of conductors has a lower impedance than the associated EGC size would.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  9. #9
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    2,083
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It did to me, too, because all my apprenticeship years were for places that spec'd the wire EGC, so it was normal for me. Now, people pay me to just make it work, and I'm the one buying and pulling the wire, so....
  10. #10
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,629
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by peter d View Post
    Seen many from the time period you mentioned with poorly supported raceway contributing to broken fittings resulting in loss of EGC, also seen loose set screws or compression nuts, but that is all workmanship issues more than anything IMO. Have seen poorly made up EGC's in cable wiring methods as well - open continuity is still open continuity.
    I do a lot of grain storage bins and handling equipment. Generally all steel structures and equipment. I do run EGC's in flexible conduits or in any non metallic raceways (which is usually just underground raceways in these applications) but see running any wire EGC in most of said systems as pointless, the equipment/structures are very effective fault return path, and usually more effective than my raceways, so if a fitting didn't get tightened it doesn't really matter much from equipment grounding perspective.