    push-on grounding clips

    Are the push on grounding clips that can be used for box bonding as required by 250.148(C) listed items?
    If so, does anyone know what UL category covers them?
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  2. #2
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,609
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    These NSI clips have a UL stamp on them.

    Roger
    Moderator

  3. #3
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    623
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    Are the push on grounding clips that can be used for box bonding as required by 250.148(C) listed items?
    If so, does anyone know what UL category covers them?
    They are covered under UL category KDER.

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    24,057
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by packersparky View Post
    They are covered under UL category KDER.
    I thought they would be but when I look up Raco's part number for that clip, it does not show up in the list of part number that they have listed in the category.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  5. #5
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    24,057
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    These NSI clips have a UL stamp on them.

    Roger
    Thanks. However they can't be used in the field as they are UL Recognized and not UL listed.
    http://www.nsiindustries.com/UserFil...rounding17.pdf
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  6. #6
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,581
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    Thanks. However they can't be used in the field as they are UL Recognized and not UL listed.
    http://www.nsiindustries.com/UserFil...rounding17.pdf
    I note they carry the “Listed” rather than “Recognized” UL mark on the clip itself.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.

  7. #7
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rbalex View Post
    I note they carry the “Listed” rather than “Recognized” UL mark on the clip itself.
    It may be both listed and recognized.
    Bob

  8. #8
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    24,057
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    It may be both listed and recognized.
    It does not appear on the list of their products that are listed under that category.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  9. #9
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    24,057
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rbalex View Post
    I note they carry the “Listed” rather than “Recognized” UL mark on the clip itself.
    That is interesting as that part number is not on the list of UL listed parts under KDER.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  10. #10
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    That is interesting as that part number is not on the list of UL listed parts under KDER.
    why don't you ask them?

    My guess is that it would be covered under option 7 in 250.8

    250.8 Connection of Grounding and Bonding Equipment.
    (A) Permitted Methods. Equipment grounding conductors,
    grounding electrode conductors, and bonding jumpers shall be
    connected by one or more of the following means:
    (1) Listed pressure connectors
    (2) Terminal bars
    (3) Pressure connectors listed as grounding and bonding
    equipment
    (4) Exothermic welding process
    (5) Machine screw-type fasteners that engage not less than
    two threads or are secured with a nut
    (6) Thread-forming machine screws that engage not less than
    two threads in the enclosure
    (7) Connections that are part of a listed assembly
    (8) Other listed means
    Listed assemblies can include assemblies that are field assembled. In any case, the code does not require ground screws to be listed, or terminal bars for that matter.
    Bob