    GEC/System bonding jumper thru same lug for SDS

    Any potential violatIons on taking an GEC (coming from bldg steel for example) through a Single lug on XO and loop it thru and hit xfmr enclosure to also serve as the system bonding jumper? Say it’s a 75kva 480v to 208v xfmr typical setup, with bonding done inside xfmr. Looking thru 250.24 I don’t see that it would be. Correct me if I’m wrong


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by dvpvic View Post
    Any potential violatIons on taking an GEC (coming from bldg steel for example) through a Single lug on XO and loop it thru and hit xfmr enclosure to also serve as the system bonding jumper? Say it’s a 75kva 480v to 208v xfmr typical setup, with bonding done inside xfmr. Looking thru 250.24 I don’t see that it would be. Correct me if I’m wrong


    Sent from my iPhone using Tapatalk
    I see nothing wrong with it.
    Bob

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,142
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Nope I do it quite often.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted