User Tag List
Results 1 to 5 of 5
Thread: Bonding of Instrument stands to ground grid
  1. #1
    Join Date
    Oct 2018
    Baton Rouge
    Posts
    110
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Does the NEC require instrument stands with transducers, transmitters, etc @ 24VDC and under 1A, to be bonded to the ground grid in a Class I Division 2 area?
  2. #2
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What is it that you are calling an instrument stand?
    By bonded to the ground grid do you mean that an equipment grounding conductor should be run out to the stand with the circuit conductors and somehow bonded to that stand or are you suggesting some kind of conductor that should be connected to Earth?
    Bob
  3. #3
    Join Date
    Oct 2018
    Baton Rouge
    Posts
    110
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    250.112(I) states the circuit doesnt need to be grounded if its Class 2 wiring under 50VDC - however, our inspectors want to see the stand - galvanized C6-channel - bonded with #2AWG down to the equipotential ground grid which is a buried #4/0 bare copper and runs throughout the entire Plant - mostly Class I Division 2, C & D.
  4. #4
    Join Date
    Feb 2003
    Illinois
    Posts
    24,057
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Isaiah View Post
    ... - however, our inspectors want to see the stand - galvanized C6-channel - bonded with #2AWG down to the equipotential ground grid which is a buried #4/0 bare copper and runs throughout the entire Plant - mostly Class I Division 2, C & D.
    Fairly common heavy industry/ petrochem project specification. There is no code requirement for that.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  5. #5
    Join Date
    Oct 2018
    Baton Rouge
    Posts
    110
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    Yep that’s what I thought