    How to prove a pool is bonded and grounded after the fact?

    So, my pool was installed and the concrete contractor poured the cement before the electrical inspector came through. The city is now saying that the cement needs to be torn out. Is there a way to demonstrate (reliably) that the pool and its systems and metal surfaces were grounded and bonded properly?

  2. #2
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,466
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I am approving this post, although the poster is not a member of the electrical industry. This is not a DIY question, but rather a question of what can or cannot be done. That said, I am afraid that I do not know the answer to the question. Perhaps there is some type of radiograph or metal detection that might help.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  3. #3
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    the short answer is no as grounding and bonding requirements are not performance based.

    the long answer might involve things like whether the inspector would accept evidence such as pictures and whether such pictures actually existed, or some of the things charley mentioned.

    it seems to me that whomever got the permit is responsible to pay to do whatever it takes to deal with it. you should stay out of it or it will rapidly become your problem.

    BTW, what concrete was poured that is in question? It might be possible for whomever is on the hook to cut slots in deck type concrete and install new bonding wires than to screw around a lot.
    Last edited by petersonra; 02-04-19 at 03:01 PM.
    Bob

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    eta

    since the connections only have to be made in a few spots it might be possible to open up the concrete in those spots, inspect the connections, and then repair the concrete. the inspector might accept that idea as well, especially if it were accompanied by sworn affidavits from all concerned.
    Bob

  5. #5
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,451
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Mike holt has three videos on this. They are all free- here is no 3 https://www.youtube.com/watch?v=Q8YLcXRo-Go
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  6. #6
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    Mike holt has three videos on this. They are all free- here is no 3 https://www.youtube.com/watch?v=Q8YLcXRo-Go
    that does not prove it was done to code though.
    Bob

  7. #7
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,451
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    that does not prove it was done to code though.

    I know but that is the best you can do. Too bad they didn't take pictures but if they see the correct wire size it may be enough to avoid tearing it up.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  8. #8
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    I know but that is the best you can do. Too bad they didn't take pictures but if they see the correct wire size it may be enough to avoid tearing it up.
    no. that is not the best you can do since it does not even remotely show that the pool was done to code. what inspector would accept the idea that because it met some performance standard that is not part of the code that it would meet code requirements? My guess is that many new pools would meet the performance standards of the videos with no bonding at all just due to being damp most of the time.
    Bob

  9. #9
    Join Date
    Mar 2014
    Location
    Park Ridge, NJ
    Posts
    137
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jsarconi View Post
    So, my pool was installed and the concrete contractor poured the cement before the electrical inspector came through. The city is now saying that the cement needs to be torn out. Is there a way to demonstrate (reliably) that the pool and its systems and metal surfaces were grounded and bonded properly?
    An inspector told me some time ago how he was not called for the bonding inspection prior to patio installation. He was called for the final and saw the patio installed. Required the contractor to tear it up.

    In your case, the contractor who's responsible for the patio, is also responsible for the inspections. So if it must be torn up, it's on HIS dime.

    I would say you could find a spot in the pour where the wire mesh or rebar is accessible (if they used either one) and perform a bond test to any other metallic items connected to the pool for verification.

    Some mason contractor these days are using concrete with fiber mixed in to do away with mesh or rebar.

    No matter what, the bare #8 copper must be around the pool's perimeter and be connected to the pool in 4 spots. That's probably the inspectors gripe-understandably.

  10. #10
    Join Date
    Jan 2009
    Location
    CT
    Posts
    34
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Mystic Pools View Post
    An inspector told me some time ago how he was not called for the bonding inspection prior to patio installation. He was called for the final and saw the patio installed. Required the contractor to tear it up.

    In your case, the contractor who's responsible for the patio, is also responsible for the inspections. So if it must be torn up, it's on HIS dime.

    I would say you could find a spot in the pour where the wire mesh or rebar is accessible (if they used either one) and perform a bond test to any other metallic items connected to the pool for verification.

    Some mason contractor these days are using concrete with fiber mixed in to do away with mesh or rebar.

    No matter what, the bare #8 copper must be around the pool's perimeter and be connected to the pool in 4 spots. That's probably the inspectors gripe-understandably.
    Had a inspector in town yrs ago who said he didn't see the rebar in the gunite pour of inground pool. He told contractor to chop it up. Contractor then proceeded to punch out the inspector. Hope this doesn't come to this.

    There must be the #8 wire showing back at pool filter if he did it right.