    I installed 4.5kw, 277V, single phase water heater with branch circuit breaker size of 30A.
    Inspector flagged it and says should be 25A.
    I cannot find 25A circuit breakers. All sizes found are 20 or 30A. Does anyone know of any? Are they hard to find? Does nec 2014 article 240.6 standard overcurrent sizes apply to fuses and certain type of breakers?
  2. #2
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    2,083
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    25A breakers are a standard size, even if not nearly as common. A REAL electrical warehouse will have them, or even especially Amazon, like this one: https://smile.amazon.com/MP225-25-Am...ircuit+breaker
    You are asking about how to find a circuit breaker, and don't even tell us what brand and type so we can help.
  3. #3
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    368
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MAC702 View Post
    Breaker you posted is rated for 240V. I have 277V single phase.
    Sent from my SM-G935U using Tapatalk
  4. #4
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    2,083
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    Was just a quick example to show 25 as a standard size.
    https://smile.amazon.com/SCHNEIDER-E...ircuit+breaker
    There's another one. Can't help further because we still don't know what brand you need. But the point is they are standard and available, even if not common.
  5. #5
    Join Date
    Apr 2017
    USA
    Posts
    282
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Look at 420.11(E) for over current protection. If you have a over current protection marked on the water heater use that as your OCPD if not you have to multiply your amps x 1.5 if your amps are more than 13.3A and no over current marking on the device.If it doesnt correspond to standard OCPD you can select the next size up. In your case 4500/277=16.25x1.5=24.36 and next standard size is 25A.
  6. #6
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    368
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit1 View Post
    420.11(E) applies to appliance like toaster etc not to water heater.
  7. #7
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,736
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What kind of panel, what style of breaker?
  8. #8
    Join Date
    May 2018
    Eden, NC
    Posts
    60
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    "listed" breaker is for specific panel. Just get a "classified" breaker if not sure.
  9. #9
    Join Date
    Dec 2015
    Texas
    Posts
    195
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    My experience has been a water heater this size would meet the 422.13 requirement and only be permitted to be sized at 125%. Nonetheless, it still calculates to the 25A OCPD, but you can see how it might change depending on what number you plug in.
  10. #10
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    3,071
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Fact: While 25 amps is a standard breaker size, it is not available in all breaker configurations, for example a Square D QOB 10KAIC is available, but a 22KAIC one is not. They are not available in an GFCI configuration in many panels. When you run in to that, it stinks. You basically have to install a fused disconnect in lieu of a breaker. I have usually had success in passing the cost for this on with the proper argument.