220.14(G) Show Window Load Question

Status
Not open for further replies.

gray.one

Member
Location
Reston, VA
d1ed693730a25eb015955c1573ff6e0a.jpg


Am I reading this right? You get to decide to use 200VA per ft or 180VA per 12 ft.

I must be misunderstanding something.


Sent from my iPhone using Tapatalk
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The second option gives you relief for the case where you choose to put one duplex every six inches or use a closely receptacle strip.
For the first option, IMHO, if you install extra receptacles to keep cords short you have to count them all.
 