    https://cleantechnica.com/2014/03/14...kit-truly-diy/
    I've come across this website for a plug solar panel kit, any code reference that these equipment must comply?
  2. #2
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,903
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by HecThor View Post
    Don't do it. They are just wrong in so many ways.
  3. #3
    Join Date
    May 2011
    Posts
    5,151
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If they are 'installed' they need comply with 690 and 705, to begin with, and they don't. You can be sure the equipment is not UL listed either.
  4. #4
    Join Date
    Aug 2018
    Philippines
    Posts
    23
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ggunn View Post
    I agree
  5. #5
    Join Date
    Aug 2018
    Philippines
    Posts
    23
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    Haha, exactly "they don't"
  6. #6
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    2,083
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for that link. The comments were a good read.
  7. #7
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,176
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    So far I have seen only one "plug-in" solar solution that was actually NEC compliant. It used a non-standard socket on a dedicated circuit which had to be installed for the purpose by an electrician (who was therefore responsible for permit, inspection, 120% rule compliance, etc.)
    Once the receptacle was in place, the homeowner could then plug in the packaged system which he dropped in place (considered a UL-approved product, so arguably no permit required for that part of the installation) to that receptacle. The non-standard plug connector was part of the panel and inverter package.
  8. #8
    Join Date
    Mar 2003
    Vermont
    Posts
    2,263
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    from the site comments>>>>>
    The inverters and panels for all of our grid-tie kits are UL-1741 approved,
    The inverter is manufactured in China, and the manufacturer name is Beijing Kinglong New Energy, KLNE series, and model name Sunteams.
    Approval for the method of connection is left to the utility companies. In many states, the AC male plug connection has been approved. In a couple states, it has not been approved, and the kit must be connected directly to the electrical box, adding one more step to the connection process.
    ~RJ~
  9. #9
    Join Date
    May 2011
    Posts
    5,151
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I guess there are only a 'couple states' that don't follow some version of the NEC.
    This is a scam, and a potentially dangerous one if a customer pushed the limits.
  10. #10
    Join Date
    May 2011
    Posts
    5,151
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    It is hardly the case that UL approved equipment doesn't require a permit to install.