User Tag List
Results 1 to 4 of 4
Thread: Missing EGC
  1. #1
    Join Date
    Sep 2015
    Williston, Vermont
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Missing EGC
    I have an existing 480 volt 3 phase 20 mp circuit to a roof exhaust. I need to replace the blower motor. There are [3] phase conductors in 1/2 EMT with no EGC. Is it OK to use the EMT as an equipment ground or should I run a new green conductor? I'm in a steel building, can I just ground the motor to the building frame? It's about a 300 foot run so running a new wire in the 1/2 EMT won't be easy. Thanks
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    17,610
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Read 250.118
    Roger
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,142
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Nomad86 View Post
    No, you need an EGC. It can be the raceway if it complies with Roger's code reference.
    Rob
  4. #4
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,514
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Code support for Post 3: See 250.136(A)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.