Prior to the 2017 code, conduit bodies of the same trade size as the conduit were permitted between the enclosure that requires sealing and the seal fitting.
2014 501.15(A)(1) ... Only explosionproof unions, couplings, reducers, elbows, capped elbows,
and conduit bodies similar to L, T, and Cross types that are not larger than the trade size of the conduit shall be permitted between the sealing fitting and the explosionproof enclosure.
That permission to install conduit bodies between the enclosure and the seal was removed in the 2017 edition of the code.
2017 501.15(A)(1) ...Only explosionproof unions, couplings, reducers, elbows, and capped elbows that are not larger than the trade size of the conduit shall be permitted between the sealing fitting and the explosionproof enclosure.
Don, Illinois
(All code citations are 2017 unless otherwise noted)