    Sizing the conductor for a Chiller

    Hi, my name is Ammar and this is my first post in this awesome forum,

    I already know that to size a conductor for an A.C. equipment i should have the following (as per 440.4.(B)):
    1. The minimum Circuit ampacity.
    2. The maximum Over current Protection.


    in my case I already have these values (678.48 A and 950 A respectively).

    now, when I go to table 310.15.B.2.1 NEC 2011, I can't find the value that I am looking for in the 60C column, the last value in the 60 c Column is 448A!!
    my question is:
    1. how do I size my cable for the chiller specifically?
    2. how do I size cables for high currents in general?


    Thanks for reading all this.
    Regards,
    Ammar

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,359
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Most of us don't have the P.E. after our names so we don't get to use the "B" Tables as they are for engineer specs.
    In the every day world we would use 310.15(b)(16).
    For high currents, the conductors are often paralleled so for that current it would likely be supplied by (2) 500 kcmils or (3) 4/0s.
    As you know, it gets a bit more complicated due to derating if you parallel in the same raceway or i you have high ambient such as rooftop temperatures.

    I would assume, under engineered supervision, you could follow the same plan in the "B" Tables. Keep, in mind, installation of cables larger than 500 has a degree of difficulty that often leads one to paralleleing
    Last edited by augie47; 02-09-19 at 10:44 AM.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,775
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by AmmarAbdou View Post
    Hi, my name is Ammar and this is my first post in this awesome forum,

    I already know that to size a conductor for an A.C. equipment i should have the following (as per 440.4.(B)):
    1. The minimum Circuit ampacity.
    2. The maximum Over current Protection.


    in my case I already have these values (678.48 A and 950 A respectively).

    now, when I go to table 310.15.B.2.1 NEC 2011, I can't find the value that I am looking for in the 60C column, the last value in the 60 c Column is 448A!!
    my question is:
    1. how do I size my cable for the chiller specifically?
    2. how do I size cables for high currents in general?


    Thanks for reading all this.
    Regards,
    Ammar
    I can't find you reference to the 2011 NEC.

    But using standard Table 310.15(B) (16); 75 deg C column, without any adjustments or considerations for installation method you could use 2 parallel sets of 400KCMIL (670A)
    "Just because you're paranoid, doesn't mean they're not out to get you"

  4. #4
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,359
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kingpb View Post
    I can't find you reference to the 2011 NEC.

    But using standard Table 310.15(B) (16); 75 deg C column, without any adjustments or considerations for installation method you could use 2 parallel sets of 400KCMIL (670A)
    One small problem: His MCA is 678
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  5. #5
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,775
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    One small problem: His MCA is 678
    oops, my dyslexia thought it said 668A.
    "Just because you're paranoid, doesn't mean they're not out to get you"

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    39,614
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kingpb View Post
    I can't find you reference to the 2011 NEC.
    Look in Annexes.
    I live for today, I'm just a day behind.