    Saw this in an attic... 2 fuses. The connections at the top go into am ampere meter. Any insight into this would be appreciated.
    Attached Thumbnails Attached Thumbnails Click image for larger version.
ID:	22275   Click image for larger version.
    Tony Shupenko, PE
  2. #2
    Join Date
    Apr 2015
    phoenix az
    Posts
    288
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    what is/was it feeding?
  3. #3
    Join Date
    Nov 2003
    New Jersey
    Posts
    657
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rambojoe View Post
    Don't know... likely lighting and receptacles.
    Tony Shupenko, PE
  4. #4
    Join Date
    Feb 2003
    Pennsylvania
    Posts
    2,721
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Not very consistent with the colors they used for the ungrounded and grounded conductors
    The inline fuse for the duplex receptacle mounted above the amp meter
    The amp meter in in series with the ungrounded conductor top left BX cable, feeding something not in the picture
  5. #5
    Join Date
    Feb 2003
    Pennsylvania
    Posts
    2,721
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tonype View Post
    my first thought was some type of motor repair station but the rec above the amp meter is not tied to the amp meter
    have no idea
  6. #6
    Join Date
    Jun 2003
    Hawthorne, New York NEC: 2014
    Posts
    4,449
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    No, it appears that the receptacle is and is fed through the fuse holder and that purple jumper. The cables, one going down and the other off to the right are loads also.
    -Hal
  7. #7
    Join Date
    Sep 2009
    Posts
    1,248
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It is very homemade and non standard. Most likely it is something that the homeowner should be advised, take it out. After disconnecting it, if you find it fed something that you still need, you can consider repowering the load.
    The meter belongs in a curio collection. The installation was not done by a regular trade contractor. It's a unicorn.
    Lasciate ogne speranza, voi ch'intrate
  8. #8
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,918
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    To either reiterate or add to the above, in no particular order:
    It's a 120v "service" with an ammeter, not a watt-hour meter.
    Could be a "sub-panel" not the service; check other side of wall.
    Feed coming in from upper-left cable coming through the wall.
    The conductor coloring is not consistent throughout installation.
    Top of the enclosure was butchered to accommodate ammeter.
    Both ungrounded and grounded conductors switched and fused.
    Receptacle above is also used through fuse-holder on bottom.
    Service rating appears to be stuck through on label on door.
    It's probably better and safer than some wiring I have seen.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  9. #9
    Join Date
    Feb 2003
    Pennsylvania
    Posts
    2,721
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Never thought of a service in an attic space, could be though its old enough
  10. #10
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,603
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Agree with larry, likely is 120 volt supply, from the top left cable. Look carefully the black conductor goes to top left terminal of disconnect. White disappears on us but pretty sure is the one landing on left ammeter lead, then right ammeter lead lands on the top right terminal of disconnect. Lots of old installations had fuse in both lines, some may not even been grounded originally and maybe part of reason why fuse in both lines. They are metering the white supply lead (whether it is grounded or not).