All,

Can someone tell me if I have wired up N.O. contact correctly on attached PDF? Does +24vdc land on common terminal or NO terminal? Does it matter on a dry contact? Any links or explanations on this matter would be appreciated.

Thanks in advance,
DavidThanks in advance,
David
 

Attachments

  • DI level connection.pdf
    42.8 KB · Views: 0

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
All,

Can someone tell me if I have wired up N.O. contact correctly on attached PDF? Does +24vdc land on common terminal or NO terminal? It will work correctly either way. Does it matter on a dry contact? Any links or explanations on this matter would be appreciated.

Thanks in advance,
DavidThanks in advance,
David
Your plant may have a convention they follow, but as far as actually working it does not matter.
 