    Table 430.52

    If I have a moter FLC 10hp 208 volt is 30.8, sizing inverse time breaker 2.50% table 430.52.
    FLC 38.8x2.50%= 77 amps next size up 80 amp. My wire size would be FLC amps 30.8x1.25=
    38.5 number 8 awg wire, I’m I doing this right it seems wrong 8 awg wire on a 80amp breaker?

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,506
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by 624 View Post
    If I have a moter FLC 10hp 208 volt is 30.8, sizing inverse time breaker 2.50% table 430.52.
    FLC 38.8x2.50%= 77 amps next size up 80 amp. My wire size would be FLC amps 30.8x1.25=
    38.5 number 8 awg wire, I’m I doing this right it seems wrong 8 awg wire on a 80amp breaker?
    Read 240.4, then 240.4(G) and Table, then back to the appropriate part(s) of 430.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,272
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Remember that your motor will have overload protection so the wire is protected. The breaker is there for short circuit or ground fault protection only.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    3,000
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Larry sent you to the appropriate code section to tell you that the answer to your question is yes. Dennis told you why. I thought I would let you know because sizing a wire that way is scary until you know you are right. I have only seen an engineer size a motor feeder to these tables a couple times in my career. They usually size them to the feeder breaker. A similar over-engineered thing is the size grounding electrode conductor (250.66) for a concrete encased electrode our a pair of ground rods.


    I know what I don't know, and I know where to go to find it!

  5. #5
    Join Date
    Feb 2019
    Location
    Fresno ca
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ok thanks a lot