User Tag List
Page 2 of 2 FirstFirst 1 2
Results 11 to 17 of 17
Thread: Current Measured on water and gas lines
  1. #11
    Join Date
    Jul 2015
    Wilmington, NC USA
    Posts
    499
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are these overhead or underground services? Also, can you confirm (visual) that both houses are served from the same transformer?
  2. #12
    Join Date
    Feb 2003
    Illinois
    Posts
    24,057
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    I find the older I get, the dew brain cells are firing, but would that be the case since he's showing current with the main "Off".
    I would tend to think the problem might be more outside of his area with the current flowing back thru the pipe his neutral to the transformer.
    There may be more than one issue, but with a 3 amp increase when a load in the building it turned on, there is no question in my mind that there is a problem with the service neutral that serves that building. It would be highly unlikely that the current increase on the water pipe, as a result an issue at a different building, would occur at the same time he added load in his building.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  3. #13
    Join Date
    Feb 2003
    Illinois
    Posts
    24,057
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Try to get the utility to use a "beast" tester at the meter if they have one.
    https://hjarnett.com/products/manufa...s/super-beast/
    Don, Illinois
  4. #14
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,514
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  5. #15
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,959
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    There may well be a neutral issue feeding more than one house, making it between the utility transformer and the distribution points.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  6. #16
    Join Date
    Mar 2003
    Vermont
    Posts
    2,264
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    M.E.N. in close proximity w/metallic municipal systems all common to the serving xformer....?
    ~RJ~
  7. #17
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,643
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you have continuous metal piping connecting to all houses in the neighborhood and all of them are bonded to the electrical service grounded conductor - you have a huge network of parallel paths. Even if there are multiple transformers in the neighborhood, they are all bonded together via a MGN. There is somewhat unlimited number of paths for current to flow.
    When you have parallel paths current takes all those paths. The lowest resistance path carries the majority of the current but all paths do carry some current. This is why even when OP has the main breaker open, there is still some current on the water line, it is current from that network and the portion of it that happens to be flowing in that path. As long as that network remains intact there is nothing you can do to prevent those currents from straying throughout the network. The biggest danger here is for the plumber that opens the path when working on the piping.
    Since 1996 NEC we have been required to run GEC to the first five feet of piping after it enters the structure. This does help limit that current path to only the first five feet of piping into the structure, and the risk to the plumber typically only involves first five feet of pipe or if they would be opening something outside the house in the main supply.
    If this is an older application that has the GEC landed somewhere besides within first five feet of entry - you can move the GEC to within first five feet and that will at least remove current from other piping through the house, presuming there is no second pipe leaving the house that makes up an additional path in the neighborhood network, metallic water line to an outbuilding that also has electricity on same property would be an example that might still leave you with troubles.