    700.8 Multiple panels from MDP

    Greetings,
    I’m finishing up a hospital expansion and the engineer has spec’d a SPD on all of my emergency panels. Is the code to be taken literally or will a single SPD on the distribution panel of each system satisfy the requirement? Seems like triple redundancy with one on the MDP, the high voltage and the low voltage of the same system.
    Thanks for your insights.

  2. #2
    Join Date
    May 2018
    Location
    Ohio
    Posts
    375
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Take it literal. Hv and lv are not even connected electrically except through ground connections. And if lightning hits the opposite end of the building of where main is, surge will fry that wing even if you have spd at other end of building, lightning doesn't follow a ladder diagram

  3. #3
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,883
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by PSDNCDOLFAN View Post
    Greetings,
    I’m finishing up a hospital expansion and the engineer has spec’d a SPD on all of my emergency panels. Is the code to be taken literally or will a single SPD on the distribution panel of each system satisfy the requirement? Seems like triple redundancy with one on the MDP, the high voltage and the low voltage of the same system.
    Thanks for your insights.
    I've always been under the impression that it means literally all panelboards.