Originally Posted by
Richard S
The relays are SEL751A and each relay has the potential to feed (3) transformers. We are not the EOR for this project, but are trying to provide some guidance. The drawings actually show 1200A circuits (3x500kcmil AL MV-105 25kV per phase) if you can believe that. I think they did that because the VCB's are 1200A rated and not knowing that the relay settings will dictate the overcurrent values. Thats the only think I can think of. That's 43MVA of conductors for each circuit when you have a maximum of 12MVA of connected load.
Do you know where it may state about using the fan assisted rating? It make sense to me, but I would like to have some back-up. I looked through the RED book (IEEE-141) and a few application guides, but could find anything specific to that.