    SKM Generator model

    Admittedly I am not an expert in either generators or SKM software. I am modeling a power system in SKM and I have been told that our generator is 1750kVA, 0.7PF rated. This results in 1225KW but I do know that the engine powering the gen is only 1000kW. Generator model in SKM only accepts kVA and PF; should I adjust the kVA for the engine and enter 1428kVA, 0.7PF?

    Thanks,
    "Because it's there!"
    George Mallory

  2. #2
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,836
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Very unusual for a 0.7 pf rating. You might want to check

    For SKM, if the pf is that weird, you likely need alternator info such as the x"d for contribution info.
    Ron

  3. #3
    Join Date
    Aug 2010
    Location
    Texas
    Posts
    306
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ron View Post
    Very unusual for a 0.7 pf rating. You might want to check

    For SKM, if the pf is that weird, you likely need alternator info such as the x"d for contribution info.
    what is weird about the PF? Is it too low? Nonetheless that was not my question; I was wondering if I should enter Gen rating based on engine rating. Gen is rated 1750kVA but engine output is only about 1000kW.
    "Because it's there!"
    George Mallory

  4. #4
    Join Date
    May 2010
    Location
    North of the 65 parallel
    Posts
    2,389
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Nope you did not ask about the pf. However:
    Most every 3ph alternator of any size (say over 100kVA) is rated for KVA at .8pf lagging. I recall only two (maybe?) in the last 50 years that wasn't .8pf. Which makes your alternator suspect that it will perform as might normally be expected.

    As for the value to enter, if your concern is short circuit currents, then I would suggest using the alternator nameplate data.

    Since you "Know" the driver is 1000kw, I would suspect nameplate data that you "have been told".
    Without data you’re just another person with an opinion – Edwards Deming