    UFER gone after framing

    Get to new residential build to install permanent service. Find that the framers cut off the UFER flush with the top of the poured wall and installed the pressure treated
    2"x8" top plate over it.

    Will 2 driven 5/8" x8' galvanized rods suffice for the Grounding electrode?
    Incoming water is plastic.

    Can the AHJ require that a CEE be put in after the fact?

    Thanks

  2. #2
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,283
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by nizak View Post
    Get to new residential build to install permanent service. Find that the framers cut off the UFER flush with the top of the poured wall and installed the pressure treated
    2"x8" top plate over it.

    Will 2 driven 5/8" x8' galvanized rods suffice for the Grounding electrode?
    Incoming water is plastic.

    Can the AHJ require that a CEE be put in after the fact?

    Thanks
    The CEE still exists. You have to use it. The piece of rebar the concrete guys left for you is just for your convenience. It is not part of the CEE.

    You need to let the GC deal with this financially.
    Bob

  3. #3
    Join Date
    Nov 2007
    Posts
    928
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ⚒👷

  4. #4
    Join Date
    May 2010
    Location
    North of the 65 parallel
    Posts
    2,161
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Just remember
    Do not talk about any discussion topics that could/should occur with the framers.
    Otherwise words like "premeditated" get thrown around.
    Without data you’re just another person with an opinion – Edwards Deming

  5. #5
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,452
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Someone (not necessarily you) will have to chip into the foundation wall and make the connection to that rebar. Yours is unlikely to be the butt soon to be in a sling.

  6. #6
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,283
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    Someone (not necessarily you) will have to chip into the foundation wall and make the connection to that rebar. Yours is unlikely to be the butt soon to be in a sling.
    if anyone chips into the concrete it will need to be properly repaired and re-inspected. If the panelboard is in the basement it might be simpler to access the CEE connection from the inside.
    Bob

  7. #7
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,495
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    OP, was this a rebar stub or a CU wire?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  8. #8
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    7,059
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    OP, was this a rebar stub or a CU wire?
    Quote Originally Posted by nizak View Post
    Get to new residential build to install permanent service. Find that the framers cut off the UFER flush with the top of the poured wall and installed the pressure treated 2"x8" top plate over it.
    As I read this, the OP says the conductor tied to the UFER is inside the poured concrete wall that is on top of the footing.

    If I could reasonably designate the place on the wall that the Grounding Electrode Conductor is in, I'd expect them to expose enough of it to install a non-reversible crimp.
    Another Al in Minnesota

  9. #9
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    592
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by nizak View Post
    Get to new residential build to install permanent service. Find that the framers cut off the UFER flush with the top of the poured wall and installed the pressure treated
    2"x8" top plate over it.

    Will 2 driven 5/8" x8' galvanized rods suffice for the Grounding electrode?
    Incoming water is plastic.

    Can the AHJ require that a CEE be put in after the fact?

    Thanks
    Around here it is allowed to create another concrete encased electrode next to the footing with 20 feet of rebar or #4 wire encased in 2 inches of concrete. You would not have to break up concrete since the last sentence of 250.52(A)(3) states that where more than one CCE is present at a building, only one needs to be bonded to the grounding electrode system.

  10. #10
    Join Date
    Nov 2007
    Posts
    928
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It was a rebar stub.