    outlet in sheetrock encapsulated column

    hello

    will someone please tell me whether or not its code compliant to install an outlet in a sheetrock column which is encapsulating a steel column? its in a church sanctuary thanks the sheetrock is three layers thick thank you for the great help
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  2. #2
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    2,604
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    you would have to maintain the fire rating of the assembly

    https://www.nationalgypsum.com/file/...ok_May2014.pdf

    Page 86 3 hr fire rating

  3. #3
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,728
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I've done it but the columns were spray coated before and the print showed them going there; so stamped by engineers. Three layers of rock sounds like fire protection, look at fire barrier wraps. Not sure what 3 layers of 5/8 or 1/2, or 1" gives in hours.

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,875
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)

    Fixed Poster

    Since it's surround a column and there are 3 layers than as David stated you'll need to be conscious of the fire rating of the column. Metal boxes generally have a 2 hour fire rating.
    Last edited by infinity; 02-12-19 at 06:43 PM.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Oct 2007
    Location
    Piedmont region of NC
    Posts
    772
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Wow.... Thanks for all of the great replies. Babe Ruth would be proud of you all for knocking this one out of the park for me...