    Light Duty Disconnect Failure

    A Client built an apartment building with pre-fabricated modules. Entire apartments roll up on a truck and get stacked up to make a building.

    In each unit there is an air conditioner fed via a light-duty non-fused disconnect switch - the kind where you pull on a plastic handle with two pieces of copper attached. The copper is held by jaws attached to cable lugs. You can flip it over and plug it back in in the "Off" position. Disconnects have been applied within their ratings. There have been 4 failures of these disconnects. The owner found out when the tenants reported "no heat". The plastic plugs are melting.

    As a temporary measure, they've bypassed the disconnects within the box. I told them it was ok to do that because it's all within sight of the panel. But I want to advise them on how to stop this from happening. There are dozens more of these in three buildings. Here's a picture of a failed switch...
    Click image for larger version. 

Name:	20190207_141221.sm.jpg 
Views:	108 
Size:	92.6 KB 
ID:	22333

    Two of the other failed switches were left in place because they couldn't be pulled out. I have become distrustful of these switches. Is this evidence of loose cable lugs, improperly inserted disconnects or loose jaws? Anybody see this before?
    Attached Images Attached Images  
    Alternate current
    Line to ground and ground to line
    Current alternates

  2. #2
    Join Date
    May 2008
    Location
    West Chester, PA
    Posts
    630
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Here's another one where the power was off, but they couldn't pull out the plug. They just left it in place and bypassed it.

    Click image for larger version. 

Name:	20190214_095313.sm.jpg 
Views:	176 
Size:	122.8 KB 
ID:	22334
    Alternate current
    Line to ground and ground to line
    Current alternates

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,289
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Bad run of product and you got lucky enough to have all them from that same run?

    These things are cheap, but usually don't have that high of failure rate in short time like you appear to have there.

    Presuming they are used within their rating of course.
    I live for today, I'm just a day behind.

  4. #4
    Join Date
    May 2008
    Location
    West Chester, PA
    Posts
    630
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    60A switches, biggest unit is 46 total unit amps. (Heat pumps with electric backup.)
    Alternate current
    Line to ground and ground to line
    Current alternates

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,289
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JoeStillman View Post
    60A switches, biggest unit is 46 total unit amps. (Heat pumps with electric backup.)
    Do units have integral breakers? many do and most that do should be sufficient for disconnecting means.
    I live for today, I'm just a day behind.

  6. #6
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,395
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    When you say 60 amp switch, are you talking about the disconnect, or a switch internal to the a/c unit?

    That type of non-fused disconnect comes in both 30 amp and 60 amp varieties. Do they have 30 amp versions installed?

  7. #7
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,730
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The first pic shows what looks like evidence of corrosion. The second one shows the conductor insulation burned, which could be bad connections or under sized wires.

    Cheap parts always means no margin of error on installation, protection or selection processes.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,289
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    When you say 60 amp switch, are you talking about the disconnect, or a switch internal to the a/c unit?

    That type of non-fused disconnect comes in both 30 amp and 60 amp varieties. Do they have 30 amp versions installed?
    Only ones of that style I have seen that are rated 30 amps are the ones with 30 amp fuse holders. Never seen a non fused version that wasn't 60 amp rated, but I suppose there may be some out there.
    I live for today, I'm just a day behind.

  9. #9
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    2,222
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Most common cause is loose terminations, and these likely have another common denominator in whoever installed them.

    But a bad run of the product is possible, though these are pretty stupid simple and hard to make badly. You should be able to tell if they push in and pull out with a solid connection.

    I use these everyday, and install them myself when needed. I do see a few melt down and need replacing, but in no more of a percentage than fused pull-outs or breaker-style switches. So, I'm back to it's usually a loose field connection that overheats it.

  10. #10
    Join Date
    May 2008
    Location
    West Chester, PA
    Posts
    630
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    When you say 60 amp switch, are you talking about the disconnect, or a switch internal to the a/c unit?

    That type of non-fused disconnect comes in both 30 amp and 60 amp varieties. Do they have 30 amp versions installed?
    These are disconnects external to the heat pump. All are 60A and fed with #6's. There is no breaker on the unit. No upstream breakers have tripped.