Thread: Is using the main panel as a junction box a code violation?

  1. #1
    Join Date
    Feb 2019
    Location
    Saltspring Island, BC
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Is using the main panel as a junction box a code violation?

    This is my very first thread, and I hope someone has an answer...So, recently we experienced quite a few power outages and a lot of people are now buying up generators and wanting to connect them using a transfer switch to the main panel. What I am seeing is when the transfer switch is wired in with its own bank of breakers, the connections to the house are being made in the main panel (and the backed-up normal power breakers abandoned). This is usually done with wire nut connectors. Now, my understanding is that the main panel cannot be used as a junction box, but it seems this is allowed in the US. What is the alternative solution to this? A separate junction box for say 10 circuits outside of the main panel? This makes little sense to me, as the branch circuit wiring to the house will most likely be too short now...suggestions?

  2. #2
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    1,306
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    difference between NEC and .canadian codes possibly?

    NEC allows the connections within the panel box and if you were moving the panel box like six feet you can splice the wires in old box to do that without any problems. Many times the new box is next to old box when you design the generator panel box, so again, not a large problem.

    But, do not have the Canadian code book handy. Know some parts of canadian code were used in last code update in Jamaica, but not sure how many were, but the inspector here in Jamaica would allow me to move wires to new breakers using old box as a jumper... though he would prefer I pull new wire ... because we use conduits in most work I do here in Jamaica. But he would not require new wire, just prefer it...
    Student of electrical codes. Please Take others advice first.

  3. #3
    Join Date
    Jan 2019
    Location
    Canada
    Posts
    32
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yes it is against Canadian code. CEC 2015. 12-3032(1)

    The circuits would have to be removed and installed in the new panel. If they are not long enough a junction box will need to be used.

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,358
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Since this is the Canadian Forum section what Eddy posted probably applies. I can't say anymore as I don't know Canadian code.

    If NEC is what applies, one needs to look at some terminology - a panelboard is the assembly with the bus and breakers, it gets installed into a cabinet. You can make splices inside a cabinet. Kind difficult to make splices inside a breaker or the bus assembly, which are what makes up the "panelboard".
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    Sep 2016
    Location
    Belleville, ON CANADA
    Posts
    23
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I know several years ago it was ok. I started out in residential and performed several service upgrades and fuse to cb swaps where branch circuits were too short. I extended them with a joint in the panel and the ESA inspector had no problem with this. This was in the mid 2000's, I don't really keep up with current residential codes anymore but its worth checking in with your inspector.

    my $0.02

  6. #6
    Join Date
    Jan 2019
    Location
    Canada
    Posts
    32
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by BMANN06 View Post
    I know several years ago it was ok. I started out in residential and performed several service upgrades and fuse to cb swaps where branch circuits were too short. I extended them with a joint in the panel and the ESA inspector had no problem with this. This was in the mid 2000's, I don't really keep up with current residential codes anymore but its worth checking in with your inspector.

    my $0.02
    Making a splice in a panel is ok when adding to an existing installation as long as the wires and joints don’t take up more than 75% of the space.

    Using a panel as a junction box for conductors feeding through or tapping off to other apparatus, like conductors fed from another panel, is not allowed.

    12-3032 + 62-212

  7. #7
    Join Date
    Sep 2016
    Location
    Belleville, ON CANADA
    Posts
    23
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Eddy_Current View Post
    Making a splice in a panel is ok when adding to an existing installation as long as the wires and joints don’t take up more than 75% of the space.

    Using a panel as a junction box for conductors feeding through or tapping off to other apparatus, like conductors fed from another panel, is not allowed.

    12-3032 + 62-212
    Can't argue with that - although if I was the OP I would contact local inspector and get his input - if the originating panel is piped with a nipple over to the backup panel I don't think he'll have a problem with said joint. However I'm not an inspector.

  8. #8
    Join Date
    Oct 2012
    Location
    IN
    Posts
    56
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IMO the Canadian code requirement does keep the rats nest of wire nuts out of the main distribution panel.

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,358
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by DanS26 View Post
    IMO the Canadian code requirement does keep the rats nest of wire nuts out of the main distribution panel.
    Does it really matter or impact safety if you moved the rats nest to a junction box right next to main panel for those conductors too short to reach their terminal.
    I live for today, I'm just a day behind.

  10. #10
    Join Date
    Jan 2019
    Location
    Canada
    Posts
    32
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Does it really matter or impact safety if you moved the rats nest to a junction box right next to main panel for those conductors too short to reach their terminal.
    Wires that are too short to reach the breakers can be extended as long as the space does not get filled more than 75%. What can not be done is using the panel as a junction for circuits that do not originate from that panel.