Thread: 1/2 bath vent fan

  1. #1
    Join Date
    Apr 2018
    Location
    newengland
    Posts
    45
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    1/2 bath vent fan

    is one required?

  2. #2
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    2,743
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mortimer View Post
    is one required?
    That's a building code issue, but normally if you have natural (window) ventilation, a mechanical vent would not be a requirement in a dwelling

  3. #3
    Join Date
    Apr 2018
    Location
    newengland
    Posts
    45
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    nope, no window

  4. #4
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,337
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    In my jurisdiction a fan is required regardless of window being present. Check your building code.

  5. #5
    Join Date
    Feb 2008
    Location
    Texas
    Posts
    1,060
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    In mine, the window opening has to be a minimum size or a fart fan is required.

  6. #6
    Join Date
    Mar 2007
    Location
    Branson, Missouri
    Posts
    312
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The ICC codes (adopted as is) only require one if there is a tub or shower.

  7. #7
    Join Date
    Nov 2014
    Location
    MA
    Posts
    170
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    From what I can find in MA, section 1203.4.2.1 ventilation, it states a fan is required if there is a tub or shower.

  8. #8
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    2,743
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mortimer View Post
    nope, no window
    1203.4.2 Contaminants exhausted. Contaminant sources in naturally ventilated spaces shall be removed in accordance with the International Mechanical Code and the International Fire Code.

    1203.4.2.1 Bathrooms. Rooms containing bathtubs, showers, spas and similar bathing fixtures shall be mechanically ventilated in accordance with the International Mechanical Code.

  9. #9
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,231
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    What contaminant sources are there in a bathroom? Are the normal things that a bath fan would vent actually contaminants?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  10. #10
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,179
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    What contaminant sources are there in a bathroom? Are the normal things that a bath fan would vent actually contaminants?
    They are at my house.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor