    Quote Originally Posted by kwired View Post
    But it basically means the dielectric union needs to be outside the structure, if any part of that pipe enters the structure and is continuous for at least 10 feet in earth - 250.50 plus 250.52(A)(1) says you must use it as an electrode.
    So what's your point that hasn't already been stated?

    Roger
    Moderator

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    40,197
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    So what's your point that hasn't already been stated?

    Roger
    Well it started out as the dielectric union approach not being as simple as it may sound. I guess the non metallic supply line isn't normally so simple either. Simple concept, yes, but not necessarily so simple to install.