    208 3ph to 230-240 Y transformer

    Wondering if it's OK to connect a 208 3ph 230-240Y 112kva transformer to a 3phase subpanel the input current is 100amps

  2. #2
    Join Date
    Jan 2011
    Location
    United States
    Posts
    8,808
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Bill 12 View Post
    Wondering if it's OK to connect a 208 3ph 230-240Y 112kva transformer to a 3phase subpanel the input current is 100amps



    Whats the 240Y for? Your source is 208 volts and the secondary is 240Y?
    I'm in over my head...

  3. #3
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    421
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I'm curious, why that large of a transformer for a 100-amp circuit?

    If you have the proper OCP in place, I don't believe the NEC has a problem in under using a transformer's rating. I have heard that transformers might waste more energy when lightly loaded.

  4. #4
    Join Date
    Mar 2019
    Location
    Vallejo, ca
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It will feed a 3ph sub panel that is powering a bunch of 240 3ph equipment one is a 100amp welder.

    https://www.larsonelectronics.com/p-...BoCQuwQAvD_BwE

    This is the transformer they want me to get. Sorry it a 75kva not 112 that was wrong

  5. #5
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    3,456
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Bill 12 View Post
    It will feed a 3ph sub panel that is powering a bunch of 240 3ph equipment one is a 100amp welder.

    https://www.larsonelectronics.com/p-...BoCQuwQAvD_BwE

    This is the transformer they want me to get. Sorry it a 75kva not 112 that was wrong
    That transformer is single phase. You won't be able to power 240 3ph equipment with it.


    Maybe the wrong link?

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,001
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Bill 12 View Post
    It will feed a 3ph sub panel that is powering a bunch of 240 3ph equipment one is a 100amp welder.

    https://www.larsonelectronics.com/p-...BoCQuwQAvD_BwE

    This is the transformer they want me to get. Sorry it a 75kva not 112 that was wrong
    So I'm guessing that this will be a 3Ø, 3wire, 240 volt system without a neutral? If you need to supply any 120 volt loads then a 3Ø,4W Delta secondary might be better. A 240 volt Wye system has a phase to neutral voltage of 139 volts.
    Last edited by infinity; 03-14-19 at 04:09 PM. Reason: Spelling
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    Mar 2019
    Location
    Vallejo, ca
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Larson gave me 2 quotes here is the other one
    https://www.larsonelectronics.com/p-147482-.aspx

  8. #8
    Join Date
    Mar 2019
    Location
    Vallejo, ca
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    So we are trying to keep from running a new service which would entail changing a main panel to a 400amp and doing a hot tap and 200ft of new wire

  9. #9
    Join Date
    Jan 2011
    Location
    United States
    Posts
    8,808
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Bill 12 View Post
    Larson gave me 2 quotes here is the other one
    https://www.larsonelectronics.com/p-147482-.aspx
    112.5kva is the correct one.


    Yes it can be done- make sure your sub panel has straight rated breakers only and no 120 volt loads.
    I'm in over my head...

  10. #10
    Join Date
    Mar 2019
    Location
    Vallejo, ca
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    OK cool. So if they wanted 120 also could I get a transformer that would do that also?