User Tag List
Results 1 to 3 of 3
Thread: Transformer Grounding
  1. #1
    Join Date
    Oct 2015
    Vancouver BC
    Posts
    45
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This is actually embarrassing that I'm asking this, but I can't seem to find the right clauses to back it up... Major brain fart day!
    At an industrial site, we have a 600V, 3ph, 3w outdoor panel feeding over to a little temporary 600-120/208V transformer... there's a buried ground electrode around the 600V panel, but nothing at the temporary transformer location. We are running Teck cable (w/ bond wire) from the big panel to the little transformer and I can't for the life of me recall if we need to run a separate ground wire from the buried electrode at the panel to the little transformer Xo (as opposed to using the bond wire in the teck cable). I mean, I'm pretty sure we do, but I can't find the right backup info??
    Thanks!
  2. #2
    Join Date
    Jul 2006
    Posts
    8,849
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    I moved this from the Engineering forum to here because it is likely more related to CEC issues.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  3. #3
    Join Date
    Jan 2019
    Canada
    Posts
    32
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Bigjabe View Post
    Thanks!
    If the bond wire in the teck feeding the primary of the transformer is large enough to also be the ground for the secondary(#6awg),it can be used as per 2018 code. 10-212(2) and there is a good diagram in appendix B (diagram B 10-11) explaining it.