Thread: Tiny RC snubber, LC Filter for GFCI outlets?

  1. #11
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    1,075
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It's an L filter, not an LC, but it's probably small enough for your liking.
    http://www.farnell.com/datasheets/2189017.pdf

    An LC filter may have excessive capacitive current from hot to ground and may trip a GFCI.

  2. #12
    Join Date
    Nov 2018
    Location
    new york
    Posts
    616
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by drcampbell View Post
    It's an L filter, not an LC, but it's probably small enough for your liking.
    http://www.farnell.com/datasheets/2189017.pdf

    An LC filter may have excessive capacitive current from hot to ground and may trip a GFCI.
    The following LC filger is tested not to trip the gfci outlet:






    They marketed LC filter as Surge Protector Device maybe because Metal Oxide Varistor is more expensive or not available:



    It's selling like pancakes for people who need to protect their equipments from surges. But I no longer use it because the metal frame is not grounded. What if one wires inside contacts the chassis.

  3. #13
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,759
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tersh View Post
    The following LC filger is tested not to trip the gfci outlet:






    They marketed LC filter as Surge Protector Device maybe because Metal Oxide Varistor is more expensive or not available:



    It's selling like pancakes for people who need to protect their equipments from surges. But I no longer use it because the metal frame is not grounded. What if one wires inside contacts the chassis.
    Aren’t you using GFCIs? You have no equipment grounds anyway. The energized metal frame will hurt you when touched. Maybe one of the two GFCI products you use will trip, if you haven’t managed to defeat it with add on garbage from a company that makes junk.
    Tom
    TBLO

  4. #14
    Join Date
    Nov 2018
    Location
    new york
    Posts
    616
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Aren’t you using GFCIs? You have no equipment grounds anyway. The energized metal frame will hurt you when touched. Maybe one of the two GFCI products you use will trip, if you haven’t managed to defeat it with add on garbage from a company that makes junk.
    I know the product above is junk that's why I'm not using it.

    I'm arguing that all GFCI outlets that can nuisance trip from inductive kick and not leakage current are junk too hence must be removed from the market.

    I'm saying this because the Siemens 2-pole GFCI breakers never tripped. The only time it tripped was when old circuit were plugged to it and it tripped when there is existing short from wire to concrete.

    So all products must be like the Siemens breakers, never nuisance tripping. Is IEEE in charge of the standards. Want to write them and lobby for the removal of all junk gfci outlets in the market worldwide.