    sub-meter, utility meter, CT section

    Name:  ee.jpg
Views: 89
Size:  98.1 KBcan anyone tell me the different. I believe option 2 seems have some problems. The main service switch without current transformer feeding the distribution panel. Do we need separate current transformer for each meters because those panels are over 400 amp.

  2. #2
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,354
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    The metering system is subject to the utility's requirements. In my experience they will often want the metering hot sequenced if there are 6 or less disconnects. I am Not sure about the level of detail intended on the drawings: for sure there will need to be a CT cabinet at those current levels, perhaps that is just just assumed on the drawings?
    Ethan Brush - East West Electric. NY, WA. MA