User Tag List
Results 1 to 5 of 5
Thread: Welder Listing
  1. #1
    Join Date
    Mar 2019
    Cincinnati, Ohio, USA
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Welder Listing
    2017 Code 630.6 says "All welding and cutting power equipment under the scope of this article shall be listed." I have new unlisted spot welders. Does this article mean the "welder" itself must be listed or the "power" equipment / electrical components serving the welder must be listed?
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,863
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    It appears from the scope of art 630 that the equipment (welder) must be listed
    630.1 Scope. This article covers apparatus for electric arc
    welding, resistance welding, plasma cutting, and other similar
    welding and cutting process equipment that is connected to an
    electrical supply system.
    630.6 Listing. All welding and cutting power equipment
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    2,340
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tschneider View Post
    No, it only means they must be listed if you are going to use the provisions of Article 630.
    Among other things, this article allows you to use smaller conductors than for other equipment, based on the duty cycle of the machine.
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,514
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Is a spot welder even considered one of these "electric arc
    welding"?
    Rob
  5. #5
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    2,340
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A spot welder is a resistance type.
    I should say typically. When most people simple say "spot welder" it's universally short for "resistance spot welder." You can also "spot weld" with other types like arc welders.
Posting Permissions