    Temp Power

    I have a small organization that provides meals one time a year. They need an extra 200 amps on that day to utilize the extra roasters etc. required. I'm inclined to 4 or 5 temp panel setups that can be located as needed for that day fed via a 60 amp receptacle and cord. Are ready made setups available or do you build your own? 1ph 120/240v.
    Tom
    TBLO

  2. #2
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,452
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    I have a small organization that provides meals one time a year. They need an extra 200 amps on that day to utilize the extra roasters etc. required. I'm inclined to 4 or 5 temp panel setups that can be located as needed for that day fed via a 60 amp receptacle and cord. Are ready made setups available or do you build your own? 1ph 120/240v.
    what makes you think this would be code legal?
    Bob

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,413
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I install a new 400 amp service to the building, Main Breaker. A 225 feeder goes to the existing. A 100 feeder to the rooftop units. A 225 feeder goes to another ML panel that then feeds receptacles for my portable power units. What makes you think it would not be compliant?

    I could use the spider boxes for construction. That might be easier and/or better.
    Tom
    TBLO

  4. #4
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,678
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    I install a new 400 amp service to the building, Main Breaker. A 225 feeder goes to the existing. A 100 feeder to the rooftop units. A 225 feeder goes to another ML panel that then feeds receptacles for my portable power units. What makes you think it would not be compliant?

    I could use the spider boxes for construction. That might be easier and/or better.
    Well, you kinda buried the lede there on this story. I was wondering how a bunch of temp panels were going to magically find you another 225 amps of service.

    If your temp panels have permanently attached cord sets and there is OCPD protection at the temp panel sized to the cord set, I wouldn't see a problem, at least electrically.

  5. #5
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    794
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the set up is the same each year, I wonder if you would be better off just installing some receptacles at the required location? Sure save on dragging cords all over the place. Of course this depends on what the conditions are for getting the conduits to these locations.

  6. #6
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,413
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    Well, you kinda buried the lede there on this story. I was wondering how a bunch of temp panels were going to magically find you another 225 amps of service. Yes, minor details.

    If your temp panels have permanently attached cord sets and there is OCPD protection at the temp panel sized to the cord set, I wouldn't see a problem, at least electrically.
    I told them to continue with the generators or move the annual supper to a location that has already offered free use of its space. Old timers, want to maintain the location where it all started.
    Tom
    TBLO

  7. #7
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,678
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    I told them to continue with the generators or move the annual supper to a location that has already offered free use of its space. Old timers, want to maintain the location where it all started.
    "We've bin here a hunnert an' thirty years, I'll be danged if'n we start movin' things around now."

  8. #8
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,452
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    if you wire the new panelboards with cords, how do they fit into the allowed usages of cords in 400.10(A)?

    Presumably you are claiming 590.4(B) allows you to use cords for the feeders, however, other than allowing you to use cords for the feeders, it appears article 590 still requires you to abide by article 400.
    Bob

  9. #9
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    794
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    if you wire the new panelboards with cords, how do they fit into the allowed usages of cords in 400.10(A)?

    Presumably you are claiming 590.4(B) allows you to use cords for the feeders, however, other than allowing you to use cords for the feeders, it appears article 590 still requires you to abide by article 400.
    400.10 (A) (10)?

  10. #10
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,413
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by oldsparky52 View Post
    400.10 (A) (10)?
    ...that would be my choice
    Tom