Thread: LED Ultra slim recessed light ? No can required , wet rated , dimmable

  1. #11
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,474
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Another thing that is nice about them is they can fit right under a joist/truss so your layout is not at the mercy of the framing.

    which is a HUGE advantage

    ~RJ~

  2. #12
    Join Date
    May 2014
    Location
    Marlborough, Massachusetts USA
    Posts
    386
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    i like to use the rough in plate for NW. There are so many good things about this product... but you need to protect the j-box and whip from the closed cell foam insulators and I may be paranoid but I worry about replacement lights because the product keeps evolving so quickly.

  3. #13
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    4,510
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by romex jockey View Post
    Cans are so last tuesday....~RJ~
    2” LED’s slowly taking over. They make them in 1000 lumen output now.

    As for the OP; I’ve used that one and the 4” version and liked them. In both instances I used them in soffits where space was limited.




    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr.

  4. #14
    Join Date
    Jul 2005
    Location
    (44.057116, -123.103394)
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    I love those things. I can't specifically comment on that brand however. I have used Lithonia and a few others. I call them rat traps. I'm trying to get that to catch on, so please call them that
    Rat traps I like that.
    I have been insisting that our guys secure that junction box.
    However they point out the installation instructions say its optional.
    Comments based on 2017 NEC unless otherwise noted.

  5. #15
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,742
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    I just installed 12 4" ones. Its cool, they now have adjustable color temp which is a nice feature. About half of them had a joist in the cutout, but again no problem with the thin ones. One thing you have to be careful about with the 4" ones though is if the joist is in just the right/wrong place, pretty much dead center, then the ballast wont fit up through the hole. That happened on one of these, but I had attic access so no problem.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #16
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    660
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tortuga View Post
    Rat traps I like that.
    I have been insisting that our guys secure that junction box.
    However they point out the installation instructions say its optional.
    IMO 314.23 says it's not optional.

  7. #17
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,401
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Is there any issue with pre-wiring for them in new or gutted-remodel work? Just a matter of careful mapping of the wire locations?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  8. #18
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,474
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Is there any issue with pre-wiring for them in new or gutted-remodel work? Just a matter of careful mapping of the wire locations?
    not with the rough in plates >>>



    ~RJ~

  9. #19
    Join Date
    Jul 2008
    Location
    North Of Tampa Fl
    Posts
    466
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Put up two more of these this weekend . What a easy install . Really like the way these look .

  10. #20
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,230
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We used some of these in a suspended ceiling last fall. Worked well. A couple weeks ago they used the newer vs with selectable settings of 3,4 or 5K. Nice.
    Tom
    TBLO