    Does anyone know where the requirement that a conduit seal needs to be rated for a horizontal installation is spelled out?
    Is this also a requirement in C1D1 locations?
  2. #2
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,624
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There is no specific Article 501 rule for installing horizonal seals; however, Section 110.3(B) requires listed or labled equipment to be installed per instuctions included with the listing or labeling. Seal fittings must be listed per 501.15(C)(1) AND their manufacture's instructions will indicate if they are suitable [Section 500.8(A)] for horizonal installation.
    Section 501.15(C) applies to seals in both Class I, Divisions 1 and 2.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.