    Grounding to Rod

    Curious of a few things. Inside a building with slab already poured

    Can EMT be used from panel to ground rod or is it code to use RGS?
    Would obviously have to penetrate slab to sink ground rod?
    Would 1/2" conduit run right to ground row with no exposed wiring showing?


    Never came across this scenario.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Capture.jpg 
Views:	70 
Size:	14.1 KB 
ID:	22758   Click image for larger version. 

Name:	Capture 2.jpg 
Views:	70 
Size:	13.3 KB 
ID:	22759  

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,499
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Technically no raceway is required if not subject to physical damage but we always use EMT for aesthetic reasons. Imagine what this would look like of all of the GEC's were run free air.

    Click image for larger version. 

Name:	20180815_091915.jpg 
Views:	131 
Size:	148.3 KB 
ID:	22760
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    24,157
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Just don't forget that you have to bond the GEC to the EMT at both ends unless you are using aluminum EMT.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  4. #4
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,904
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Technically no raceway is required if not subject to physical damage but we always use EMT for aesthetic reasons. Imagine what this would look like of all of the GEC's were run free air.

    Click image for larger version. 

Name:	20180815_091915.jpg 
Views:	131 
Size:	148.3 KB 
ID:	22760
    Rob, are those all for SDS's or something else?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,499
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Rob, are those all for SDS's or something else?
    Yes, a combination of 4-4000 amp services, common grounding risers, and multiple step up transformers within the service room.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,904
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Yes, a combination of 4-4000 amp services, common grounding risers, and multiple step up transformers within the service room.
    Cool. Very pretty.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  7. #7
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,723
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Click image for larger version. 

Name:	20180815_091915.jpg 
Views:	131 
Size:	148.3 KB 
ID:	22760
    Why does this picture make me think of a church?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Why does this picture make me think of a church?
    Needs some stained glass to go with it.
    I live for today, I'm just a day behind.

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Technically no raceway is required if not subject to physical damage but we always use EMT for aesthetic reasons. Imagine what this would look like of all of the GEC's were run free air.

    Click image for larger version. 

Name:	20180815_091915.jpg 
Views:	131 
Size:	148.3 KB 
ID:	22760
    They are going to be in free air for the last foot or so.
    I live for today, I'm just a day behind.

  10. #10
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,499
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Cool. Very pretty.
    Thanks.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted