    Feeding Control Panel

    Panel feeding control panel is in sigh as note says. I don't need disconnect per code but not sure why it says overcurrent device in control cabinet. Shouldn't the OCPD in the panel feeding the control panel be sufficient?

    Aslo would I need a neutral to feed the control panel? Thanks
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Capture.jpg 
Views:	40 
Size:	18.1 KB 
ID:	22761   Click image for larger version. 

Name:	Capture 2.jpg 
Views:	44 
Size:	30.5 KB 
ID:	22762  

  2. #2
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Note use of the word "or".
    Bob

  3. #3
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,508
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    Note use of the word "or".
    Yes I did...not sure why they say OCPD in control cabinet. Was thinking there would only be one in panel feeding control cabinet.

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Yes I did...not sure why they say OCPD in control cabinet. Was thinking there would only be one in panel feeding control cabinet.
    You can have 10 if you want
    Bob

  5. #5
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    10,924
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    They do not want multiple disconnects as in three single poles vs one three pole.

    Are there line to neutral loads in the control panel? No, then no. An equipment ground? yes.
    Tom
    TBLO

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    40,627
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Panel feeding control panel is in sigh as note says. I don't need disconnect per code but not sure why it says overcurrent device in control cabinet. Shouldn't the OCPD in the panel feeding the control panel be sufficient?

    Aslo would I need a neutral to feed the control panel? Thanks
    I see it there is likely supplemental overcurrent protection within in your control panel. They are mostly telling you you don't need the local disconnect if the branch circuit device is within sight, which is what code would require anyway.
    I live for today, I'm just a day behind.