    SABC

    Having a bit of a brain fart , can I feed the under cabinet lighting in my kitchen off the SABC or do I need to run it with the lighting circuit

    Sent from my SM-G965U using Tapatalk

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,497
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Not on the SABC.

    210.52(B)(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no
    other outlets.

    Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electric clock in any of
    the rooms specified in 210.52(B)(1).
    Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired
    ranges, ovens, or counter-mounted cooking units.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Oct 2015
    Location
    US
    Posts
    1,023
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Thought so just finished running the feed from kitchen lighting!!

    Sent from my SM-G965U using Tapatalk

  4. #4
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,957
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You can't but I would do it anyway if I were adding them after the kitchen is finished. Is one LED strip light going to overload the circuit?

  5. #5
    Join Date
    Oct 2015
    Location
    US
    Posts
    1,023
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    No but when the inspector asks me to shut off the small appliance branch circuit and the under cabinet lights go off he might say something

    Sent from my SM-G965U using Tapatalk

  6. #6
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,957
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by nickelec View Post
    No but when the inspector asks me to shut off the small appliance branch circuit and the under cabinet lights go off he might say something
    Shame on you for having it inspected.

  7. #7
    Join Date
    Oct 2015
    Location
    US
    Posts
    1,023
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by peter d View Post
    Shame on you for having it inspected.
    True

    Sent from my SM-G965U using Tapatalk

  8. #8
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,957
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by nickelec View Post
    True