    Would bus detail make sense instead of tap? Someone mentioned there might not be room for the taps connectors. Not sure that makes sense. The box would have to be sized for conduits entering top and bottom and also entering the right side, correct?

    Sent from my SM-N960U using Tapatalk

  2. #12
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,531
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Would bus detail make sense instead of tap? Someone mentioned there might not be room for the taps connectors. Not sure that makes sense. The box would have to be sized for conduits entering top and bottom and also entering the right side, correct?
    Bus detail for a #6 tap? Probably not. Yes the box needs to be sized for the riser conduits regardless of whether or not you use bus detail.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #13
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    794
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    I didn't see one that has a #600 run and a #6 tap.